I was sent these pictures of a used commercial dishwasher wanting help with connecting the electrical. I've figured out most of it but some I'm unclear on.
According to the nameplate the voltage is 120V/208-240V 3W. So they have 120V/240V power with high leg (open delta)
I know that they need to hook it up as 3-wire, 2 hots and neutral, being careful to stay off the high leg.

This is where it gets muddy for me. I know what MCA and Max OCPD
is but according to this chart I'm not sure if the MCA & Max are the same or "H" is one and "C" is the other.
The bullet marks * and ** are used to check foot notes H=hot (booster) C= Chemical (non-booster).
So I'm not sure if you use one or both. So if "H" is used it says 50A. But is that both the MCA and Max OCPD
And if "C" is used its 20A, again 20A for min and max?

I'm not even sure if their machine is both "H" and "C" or one or the other.
Mainly what I need to know is wire and breaker size for this.
According to the nameplate the voltage is 120V/208-240V 3W. So they have 120V/240V power with high leg (open delta)
I know that they need to hook it up as 3-wire, 2 hots and neutral, being careful to stay off the high leg.

This is where it gets muddy for me. I know what MCA and Max OCPD
is but according to this chart I'm not sure if the MCA & Max are the same or "H" is one and "C" is the other.
The bullet marks * and ** are used to check foot notes H=hot (booster) C= Chemical (non-booster).
So I'm not sure if you use one or both. So if "H" is used it says 50A. But is that both the MCA and Max OCPD
And if "C" is used its 20A, again 20A for min and max?

I'm not even sure if their machine is both "H" and "C" or one or the other.
Mainly what I need to know is wire and breaker size for this.