I am the electrical foreman at the Amundsen/Scott South Pole Station and am trying to solve a problem with one of the scientific experiments here. It involves two computers that will randomly freeze up with no rhyme or reason. Both computers are on UPS power which is supplied via an isolation XFMR. THD is 3.7% topps and I have recorded voltage surges of up to 180v RMS. I added a bonding jumper from the rack back to the main area grounding point which did not help. Grounding is a big problem here seeing as we are on over 9,000 feet of ice. Power for the building is three phase,480V, and a #500MCM single conductor is used to bond this building with the powerplant about a quarter mile away. I have been told that people have touched the equipment rack and received a static shock which had the same effect on the computers but most of the time no one is around when the problem occurs. Some of the solutions I have been given range from too low humidity (which is next to zero here), harmonic distortion from the UPS systems,to the obvious grounding and static build up issues. I'm not trying to fix the problem, only understand what is going on and give the engineers that are here in the summer some useful information. Thanks!!!