I have a motor that will run continuous that has the following nameplate rating, see attachment for reference.
I also typed out the key information for your use too
EDrive Rating:
Voltage Configuration: 480V/3P
Power kW: 22
Max Input Current - Amp: 52
Max Output Current - Amp: 46

Motor Rating
Max Current - Amp: 38
Power -kW/HP: 22/29.5

Motor Operating Setting
Max Power - kW/HP: 20/27

Should I use the the Max Input Current of 52A.
So 1.25*52A = 65A
Convert to kW
65A*√3*480 = 54.015kW

Would I need a 75kW Transformer based on my calculation above.
Or can I use a 30kW Transformer since the nameplate says its uses only 22kW


Motor.JPG
 
Since the drive has a voltage range, the max current will be at min voltage (380).

Operating at 480 will result in (approximately) proportionately lower current.

I roughly come up with a 50KW transformer.
 
Since the drive has a voltage range, the max current will be at min voltage (380).

Operating at 480 will result in (approximately) proportionately lower current.

I roughly come up with a 50KW transformer.
Unless this guy is from overseas, it's going to be operated at 480 so I would not be worrying about what the current will be at 380.
 
Unless this guy is from overseas, it's going to be operated at 480 so I would not be worrying about what the current will be at 380.

He used 480 in his calculations. That’s why I said to ratio the max current on the nameplate down based on his voltage.
He was using the max current (which would only be relevant on 380) along with 480V!
 
Should I use the the Max Input Current of 52A.
So 1.25*52A = 65A
Convert to kW
65A*√3*480 = 54.015kW
Use the 52 amperes. As far as the 125% factor, the NEC isn't really clear about whether it should be used or not for load calculations. Maybe someone can confirm this?

Either way, a 50-kVA transformer would be adequate as there is no code rule to size a transformer based on the "calculated load". It's common sense to size the transformer for the actual load, but it is also best practice to size for future loads/expansion (if applicable). Transformers are capable of being loaded beyond their kVA rating. Table 450.3(b) would account for overloading up to 125% before primary-only or secondary overcurrent protection would operate.
 
The 125% of the drive input current rating is only required for the conductor sizing feeding the VFD; 430.122.

I would size the transformer for the VFD input, because having to change it later when someone puts in a slightly larger fan will be a pain in the rear.
 
I would get the next size up transformer from whatever the input current to the VFD suggests. That'll almost always give you plenty of cushion
 