Help With Subpanel Circuit

Status
Not open for further replies.

mike4326

Member
Location
fort wayne,in
I am trouble shooting a problem for a customer of mine. He has a main breaker panel in his home, the previous owner ran a 240 circuit out to the garage, via underground. Problem is that just recently rather than tripping any of the breakers in the garage sub panel, it is tripping the 30 amp double pole breaker in the house. I had shut off all the 15 & 20 amp breakers in the garage sub panel and after about an hour the 30 amp breaker trips. This is starting to baffle me a bit.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
My guess is that when the feeder was run underground, it was not done properly. If the wrong type of cable was run directly buried, its insulation system may have deteriorated. That could be the cause of the trips. I don't know if there is a test you can run to check out this possibility. I don't know if a megger test would tell you anything. Do you know how long ago the feeder was run underground? The older it is, the more likely it will have deteriorated to the point of causing the trip.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you disconnect the feeder conductors completely at the remote panel, wire nut them and then turn on the 2P-30 you will be able to confirm that the problem is between the end of the feeder and the 30 amp CB.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you disconnect the feeder conductors completely at the remote panel, wire nut them and then turn on the 2P-30 you will be able to confirm that the problem is between the end of the feeder and the 30 amp CB.

Keep in mind he means to cap them individually, not as a single bundle. ;) It took me a moment to catch this.

You can also wire a high-wattage incandescent bulb in series with each pole of the breaker to act as a combination current limiter (so you the breaker can stay on) and current indicator. The bulbs should obviously be dark with the garage disconnect off unless the problem is in the garage.

You might find an issue you can correct above ground by wiggling where you have access, and look in LBs, etc.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
191114-2030 EST

mike4326:

Based on what you described you have a problem between the main panel breaker, and subpanel, including the subpanel bus bars.

This may be a large load right from when you start your test, or an abrupt overload at the time of tripping.

Allow some time for the tripping breaker to cool. Possibly 5 minutes, or at least 1 minute. This is also cooling time for the cable.

With all breakers in the garage off, and the main panel breaker off. Measure each main panel bus voltage to neutral.

With main panel breaker on, then using a current clamp-on meter measure the current on each hot line to the garage. If either line immediately has a large current, then trouble shooting is simple. A current around the trip point of a breaker won't immediately trip a breaker.

If both hots have a large current, and about equal, then you have a short between them. If only one is high, yhen check the neutral for the high current.

You have not indicated the cable length. At 60 Hz, 5000 pfd, and 120 V current would be about 120/500,000 = 0.2 milliampere. Thus, if you read a number of milliamperes of current you probably have a leakage problem. This alone and unchanged won't trip your breaker. However, after your time delay time this might change to a low resistance short.

This website is screwed up tonight. I loose what I am composing.

Let's assume you initially see a large current. Identify the wires where this current flows. May or may not be useful. At 240 V a 30 A breaker will trip with a load of approximately 8 ohms, 4 ohms at 120 V.

Do some measurements, and tell us what you see.

.
 

mike4326

Member
Location
fort wayne,in
I want to thank all of you guys for your great responses. I did have a feeling that it might be the underground feeder insulation deteriorating. I'm not sure how long ago it was installed. I'm going to isolate the feeder and do some tests tomorrow. Once again thanks
 
I am trouble shooting a problem for a customer of mine. He has a main breaker panel in his home, the previous owner ran a 240 circuit out to the garage, via underground. Problem is that just recently rather than tripping any of the breakers in the garage sub panel, it is tripping the 30 amp double pole breaker in the house. I had shut off all the 15 & 20 amp breakers in the garage sub panel and after about an hour the 30 amp breaker trips. This is starting to baffle me a bit.

Mike are you telling us that you have a 30 amp service for your garage
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Is garage only thing supplied by the breaker in main house panel? Make sure something else didn't get tapped off it or elsewhere on the circuit.

Is any current drawn when everything in garage is turned off?

Meg conductors at least twice the test voltage as operating voltage.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
He could/should pull that 30 Amp breaker in the main panel and check for arcing and arcing at surrounding breakers to see if they are really heating up.

won't hurt, but seems less likely it will trip his 30 amp breaker if it isn't carrying any load, and you would think others would be tripping if the heat is coming from other breakers.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Disconnect the cable at both ends and megger it.

With information we do have so far and presuming it is accurately given to us, I think that is what I would be doing.

Still want to know if there is any current at the feeder breaker when the circuit is open at the garage? That will either be a fault or other unknown load is connected to this feeder that might have the problem.
 