- Occupation
- Facility Senior Electrician
Would someone explain to me what this part (that I circled) of the control circuit is for? Can't seem to figure out it's purpose.

it just makes both pump stay on once PS2 is made until PS1 is not made. Otherwise as soon as PS2 turned off again the secondary pump would shut off right away.Would someone explain to me what this part (that I circled) of the control circuit is for? Can't seem to figure out it's purpose.
![]()
it just makes both pump stay on once PS2 is made until PS1 is not made. Otherwise as soon as PS2 turned off again the secondary p mp would shut off right away.
If one pump would fail, the second pump would still be started by P-S2 but stopped by P-S1. But if say M1 motor overload had tripped then you will be left with alternating cycles that start/stop with P-S1 one cycle and P-S2 the next cycle.
It could run that way indefinitely unnoticed unless you maybe connected an hour meter to each pump and monitored them to see that they are getting approximately the same run time.
Until the second pump has also failedA good point. They don't have meters and run infrequently in an unoccupied area. Little chance such a failure would be noticed.