I have a condensing unit , rla = 23 , Volts=460 phase = 3 there is a LRA = (I don’t remember right now)
Panel to feed this unit : 200a 3 phase 120/240open delta.
Question 1 : how do I calculate the transformer size to feed this CU ,is this correct? 23A (condensing unit RLA) x 480 x 1.732 = 18.32 kva == 25 kva , 120/240 delta primary , 480 Y secondary transformer . should I go for a 30 KVA?.
Question 2 : OCP , I read 450.3(b) , how do I do the transformer OCP and CU OCP ? in terms of installation , do I need a sub panel on the secondary side then feed CU and disco at the CU? , or I can go straight from transformer to CU disco , this is a dedicated transformer , just to feed this CU.
Question 3 . do I use 310.15 for conductor sizing? It’s 100ft from transformer to CU.