(2) Transformer Secondary Conductors Not Over 3 m (10 ft) Long Where the length of secondary conductor does not exceed 3 m (10 ft) and complies with all of the following:
(1) The ampacity of the secondary conductors is
a. Not less than the combined calculated loads on the circuits supplied by the secondary conductors, and
b. Not less than the rating of the device supplied by the secondary conductors or not less than the rating of the overcurrent-protective device at the termination of the secondary conductors, and
c. Not less than one-tenth of the rating of the overcurrent device protecting the primary of the transformer, multiplied by the primary to secondary transformer voltage ratio
(2) The secondary conductors do not extend beyond the switchboard, panelboard, disconnecting means, or control devices they supply.
(3) The secondary conductors are enclosed in a raceway, which shall extend from the transformer to the enclosure of an enclosed switchboard, panelboard, or control devices or to the back of an open switchboard.