I am taking the master's practice exam in the Tom Henry 2005 Calculations: Exam Questions and Answers, test 1. Question #3 is...What is the minimum demand on the service for 300 duplex receptacles in a hospital?...a)20.8kva b)27kva c)32kva d)54kva. The answer they give is a)20.8kva. They get this answer by using table 220.42. 180va x 300= 54000kva. 50000@ 40% and 4000@ 20%. I do not understand why table 220.42(Lighting load demand factor) was used instead of 220.44(Demand factors for non-dwelling receptacle loads). I am taking my Wisconsin Masters and I need to understand why this is done. I also have a question about question 13...How many #8 RHH conductors w/o outer covering can be installed in a 1 1/2ENT. I came up with 13.9, so I put the answer as 13. They have the answer as 14. I thought that 13.9 was the maximum so you had to go down. Am I not right?
[ January 28, 2006, 06:25 PM: Message edited by: marsbar42 ]