The last time I connected inverters phase to phase on a three phase service they were the old style Sunny Boys, i.e., transformer interconnected. There was a jumper to change so that they didn't use the neutral, which made sense to me, since on a 208 service line to neutral is 120V but for single phase inverters with 208V phase to phase, line to neutral for each inverter would be 104V, so their neutrals would be at different voltages from one another.
I just was handed a circuit diagram that shows three single phase inverters connected phase to phase (A-B, B-C, and C-A) to 208V with their neutrals all connected together and tied to the service neutral. How can that be? Wouldn't each inverter have to generate two 120V phase to neutral waveforms 120 degrees apart to connect that way? Or am I just having a senior moment?
I just was handed a circuit diagram that shows three single phase inverters connected phase to phase (A-B, B-C, and C-A) to 208V with their neutrals all connected together and tied to the service neutral. How can that be? Wouldn't each inverter have to generate two 120V phase to neutral waveforms 120 degrees apart to connect that way? Or am I just having a senior moment?