ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Electrical Engineer - Photovoltaic Systems
We have a project on the roof of a new condo complex that is 100+ small PV systems each feeding a single condo unit. Each unit has its own meter and 100A service disco feeding a 100A MLO MDP in one of three ground floor electrical rooms, and each MDP has a 100A load breaker that feeds a panel in the unit on an upper floor. Our systems feed the MDPs in the electrical rooms through 20A breakers. We feed the PV at the opposite end from the utility feed, the bus is qualified under 705.12(D)(2)(3)(b), i.e., the 120% rule, and everything's hunky, right?
But no; the EC installed MDPs with a weird bus that feeds L1 from one end and L2 from the other. I've never seen this but our master says they are not that uncommon. I don't see how we can qualify under any of 705.12(D)(2)(3), not even (d) since the bus is neither center fed nor multiple ampacities.
We have investigated downsizing the breakers feeding the units to 80A in order to qualify the bus under (c) but the unit load analysis the EC ran shows that we can't do that. The meter and service disco are in the same enclosure, so we can't get to the line side of the disco. The MDPs are MLO so we can't install load side taps between them and the service discos. I don't think we can interconnect via two single pole breakers each on the opposite end of the bus from the utility feed.
Whaddya think?
But no; the EC installed MDPs with a weird bus that feeds L1 from one end and L2 from the other. I've never seen this but our master says they are not that uncommon. I don't see how we can qualify under any of 705.12(D)(2)(3), not even (d) since the bus is neither center fed nor multiple ampacities.
We have investigated downsizing the breakers feeding the units to 80A in order to qualify the bus under (c) but the unit load analysis the EC ran shows that we can't do that. The meter and service disco are in the same enclosure, so we can't get to the line side of the disco. The MDPs are MLO so we can't install load side taps between them and the service discos. I don't think we can interconnect via two single pole breakers each on the opposite end of the bus from the utility feed.
Whaddya think?