What size branch-circuit short-circuit and ground fault protection is required for a 16 amp 240 volt single phase refrigeration motor compressor??
440.22 Application and Selection.
(A) Rating or Setting for Individual Motor-Compressor. The motor-compressor branch-circuit short-circuit and ground-fault
protective device shall be capable of carrying the starting current of the motor. A protective device having a rating or
setting not exceeding 175 percent of the motor-compressor rated-load current or branch-circuit selection current, which‐
ever is greater, shall be permitted, provided that, where the protection specified is not sufficient for the starting current of
the motor, the rating or setting shall be permitted to be increased but shall not exceed 225 percent of the motor rated-
load current or branch-circuit selection current, whichever is greater.
Exception: The rating of the branch-circuit short-circuit and ground- fault protective device shall not be required to be less than 15 amperes.
Read infinity’s post. ”...not exceeding...” They are both acceptable. It could be smaller.so if this were a test question would the answer be 25 amp or 30 amp? Asking for a friend
This is something that would be very rarely done in the field as almost all such equipment has the minimum circuit ampacity and the maximum permitted OCPD listed on the nameplate.