hermetically sealed motors calcs

Status
Not open for further replies.

rhamblin

Senior Member
why is it that a/c motor equipment can be fused at 225% when the conductors are computed at 125%? It seems that the conductors could burn up long before the overcurrrent kicks out.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The a/c equipment provides the overload protection, the branch circuit fuse or circuit breaker only provides short circuit and ground fault protection.
 