I think you have a mis-application on your hands. At least, something is not making sense to me. Please note that a motor does not know anything about its power source. The only thing different between a motor designed to work with a VFD and a motor designed to work with a constant 60 hertz supply has to do with bearings and/or grounding of the shaft. The motors themselves work in exactly the same way.
{ASIDE: By the way, if your motor is not designed to operate with a VFD, then you better change it out now. Otherwise, you will be changing out the damaged motor in a few weeks.}
So I have to agree with Steve: The motor can't be designed to run above 1800 RPM with a 60 hertz supply, unless it is designed to run far, far above 1800 RPM (the next step up is 3600 RPM). You might have a motor that is designed to run with a VFD, that needs to run at 1823 RPM to give you your desired CFM, that has 2 poles (not four), and that would run at 3600 RPM if you hit it with 60 hertz, and that therefore would normally run nearer to 30.4 hertz.
Finally, keep in mind that the motor does not care what you are hoping to get, in terms of CFM. It takes incoming power, and it pushes its load in circles. If you aren't getting the CFM you want, it's not the motor's fault. It's the fault of the designer(s) who selected that particular motor and fan combination.