ubbogus2

New member
Location
Spring, TX, USA
Down here in TX the 3 phase-to-phase is 240VAC. The building we are in has phase C as the hi leg (213VAC measured). We have half the breaker panel using A & B to wire 120 to offices and the other half A & B for 240 welders and such. As it is the load is severely unbalanced as all the C positions are vacant. The question is - can I use double breakers across B & C or C & A for 240VAC usage?
Thanks,
John in Spring, TX
 

Lectricbota

Senior Member
Down here in TX the 3 phase-to-phase is 240VAC. The building we are in has phase C as the hi leg (213VAC measured). We have half the breaker panel using A & B to wire 120 to offices and the other half A & B for 240 welders and such. As it is the load is severely unbalanced as all the C positions are vacant. The question is - can I use double breakers across B & C or C & A for 240VAC usage? Thanks,John in Spring, TX
Yes you can---just make sure to use 240 volt straight rated circuit breakers, and not the slash rated 120/240 breakers.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Yes, you can do this, and as lectricbota indicated you must use fully rated breakers, not slash rated IE 120/240. Couple of caveats though. Don't do this to any load that also requires a neutral such as a dryer or similar. Also keep in mind that most 240/120 3 phase PoCo transformer banks are not built for a balanced load as most are built as open delta with just 2 transformers. Usually the 2nd transformer is smaller and provided just for minimal 3 phase loads and they expect you to have most of your single phase load on the larger transformer.
 