lielec11
Senior Member
- Location
- Charlotte, NC
- Occupation
- Electrical Engineer (PE)
I designed a job and just got the hi-pot results for all 5kV cables. Most of them were brand new, but one section was spliced into an existing cable. Our specs call for 35kV DC test voltage for all 5kV cables. The testing company only raised the test voltage to 9kV for the cable spliced with existing. A couple of questions for those that do this testing on a regular basis:
In your experience, is 9kV sufficient?
If not, in your experience is there a high chance of damaging the existing cable by raising the test voltage to the 35kV range?
After the test, the cable was drained, however, after 60 seconds there was still a residual current voltage around 3-4kV on each phase. IS this a problem, or should this be expected on longer sections of cable? All other new cable sections went down to 0 in the same time period.
All input is appreciated. Thanks.
In your experience, is 9kV sufficient?
If not, in your experience is there a high chance of damaging the existing cable by raising the test voltage to the 35kV range?
After the test, the cable was drained, however, after 60 seconds there was still a residual current voltage around 3-4kV on each phase. IS this a problem, or should this be expected on longer sections of cable? All other new cable sections went down to 0 in the same time period.
All input is appreciated. Thanks.