I am fairly new to the idea/theory behind Hi-Potting power cables and was wondering if someone could help explain some results I got from a recent Hi-Pot test I had performed. The cable we tested was a 3/C SHD-GC cable rated for 5kV. We tested each of the three phase conductors up to 25kV DC stepping up the voltage in increments of 5kV and holding for a minute, and then holding the 25kV for 15min. There were two ground wires in the conductor which we tied together, and we took our positive lead from the high potter to each phase conductor (one at a time) and connected the other lead to the grounds. The cable was 2500ft long.
I'm guessing that the point of this test it to subject the cable to a voltage, and see how much current leaks (penetrates the conductor insulation) to ground? Is this correct? At 25kV the highest leakage current that we got as 135uA. Is this an acceptable reading that you would expect to see for this type of cable. What is the cut-off leakage current for detriming if the cable is bad or not? With the cable being rated as a 5kV cable, how does it allow for 25kV to be run through it, in order to perform this test?
I would appreciate any info.
I'm guessing that the point of this test it to subject the cable to a voltage, and see how much current leaks (penetrates the conductor insulation) to ground? Is this correct? At 25kV the highest leakage current that we got as 135uA. Is this an acceptable reading that you would expect to see for this type of cable. What is the cut-off leakage current for detriming if the cable is bad or not? With the cable being rated as a 5kV cable, how does it allow for 25kV to be run through it, in order to perform this test?
I would appreciate any info.