hid ballast

Status
Not open for further replies.

mtn_elec

Senior Member
I'm having some problem with a circuit of 6 outdoor lights. they are hid ballast with ignitor and ballast (no capacitor) Magnatek 1233-35u.First there was 2 lights that were going on and off every 5 to 10 minutes chech amps and when one was trying to start up it seemed that cause current to jump to 26 amps ( I had my clamp on) and tripped 15 amp breaker. I've had rebuilt both lights all of them working now but still they last 10 or 15 minutes and breaker tripps. Check all connections, trying to find any loose wiring but nothing. I haven't rebuilt all of them so here is my question. Is there a way that ballast could be causing and overcurrent? and why the starter needs to be grounded? There were some really loose in the bracket. Please help!!!
 
Re: hid ballast

there is a part of this puzzle missing. I would amprobe each one. they should only be drawing about 1/2 amp each. sounds like one of them is still having issues.

another possibility is that water has gotten into the fixtures, or a cable is broken undergound and the current is leaking through the water.
 
Re: hid ballast

Are the lamps new? What you describe can be a symptom of a bad lamp.
Are the lamps matched properly to the ballast?
 
Re: hid ballast

I would guess a bad lamp or ballast. Take a lamp from a fixture that works and try that. (I'm assuming all the lamps and ballasts are the same).

Steve
 
Re: hid ballast

There is no water in the fixtures, all the lamps are new now, I haven't change 2 ballast the rest are new, all new sockets too and they all match the light bulb.
 
Re: hid ballast

That troubleshooting guide says correction of line-current harmonics is inherent in the ballast.

But, if RMS cl/amp metering the neutral is higher than the phases, ballast harmonics could be causing that spike in amps?
 
Re: hid ballast

these 6 lights start at 8 amps total then start dropping to 5 but in 5 minutes jump to 27 amps and tripps 15 amp breaker then. Yes I've been using my fluke clamp-on 337.
 
Re: hid ballast

I would try disconnecting one at a time or open the circuit at the half way mark to isolate which set is causing the spike. Being new doesn't mean a thing. Once you have isolated out the offending fixture then change the bulb first then the starter, I have changed very few ballest so that would be my last choice.
 
Re: hid ballast

mtn_elec wrote: 6 lights start at 8 amps total then start dropping to 5 but in 5 minutes jump to 27 amps and tripps 15 amp breaker

If you can't find a bad fixutre, harmonics alone should'nt boost amps by a factor of five, but neutrals show more amps than phases for other reasons:

1) Neutral's may add amps when multiwire hots are terminated to the same phase in the panelboard. Brown-5A + Orange-5A both connected to A phase at panel board = 10 amps on neutral. *

2) Neutrals carry about the same current as phases, when using two hots with neutral of 3-phase, 4-wire, wye-connected system. 1999 NEC 220-22 Proof: Sqrt[(A^2+B^2)-(AB)] *

If all fixtures & wireing are perfect on a 3-phase wye where neutral matches both phases @ 5A, and this multiwire lands both 5A hots on the same panel phase, add another 10A for a 15A total on the neutral, leaving the more reasonable 80% neutral harmonics for a 27A total.

Micheal Holt's comments, "Now you know why white neutral conductors turn black at the neutral bar."

* According to: Holt, Micheal. Understanding the National Electrical Code. Albany: Delmar publisers, 1999. pg 188 & pg 86.

[ December 27, 2005, 06:58 AM: Message edited by: ramsy ]
 
Re: hid ballast

Sorry Rampsy but I forgot to say this is 120/240 service one phase. Tomorrow I will proceed with this troubleshooting I let you guys know what happened.
 