Hello,
Looking for some insight to a problem we are experiencing with high amperage reading on a ground wire. Lot going on here so bear with me, problem started yesterday with higher/low voltages coming into building 261V 287V 310V. While troubleshooting using a thermal imagining gun we found one branch circuit that had a ground heating up the hottest, 210 degrees, was at a UPS that feeds out to a CT scan. When we put an amp meter on the ground we had 160 amps, phases where around 250 amps, and only 4 amps on neutral. We had utility company come who confirmed high voltage was a problem from their substation and they corrected it. The amperage and the heat went down significantly but didn't go away currently values voltage 278 278 277, amperage 54 63 50, amperage on ground 41, amperage on neutral 4 amps. So when we started looking into the UPS possible being the issue we came across this see pics below. I have also attached the manual for the UPS.
Do you think this is where we are getting our imbalance from?
Answer to some questions you may have
Building transformer is Wye to Wye
CAT scan is straight 3 phase 480V that requires a Isolated ground same size as feeders and a redundant isolated ground #4
AT PANEL Isolated ground is bounded with bug to panel and redundant to ground bar
AT UPS Input isolated ground is not on grounding electrode but to the frame
AT UPS Input redundant ground is on output neutral bar but bonded to frame with that copper plate you see in pic
AT UPS Output isolated ground and redundant are also on Output neutral bar with Input redundant ground
Yes shutting down CAT scan would confirm that is where the imbalance is from but trying to find a time we can put it out of service is not easy
Looking for some insight to a problem we are experiencing with high amperage reading on a ground wire. Lot going on here so bear with me, problem started yesterday with higher/low voltages coming into building 261V 287V 310V. While troubleshooting using a thermal imagining gun we found one branch circuit that had a ground heating up the hottest, 210 degrees, was at a UPS that feeds out to a CT scan. When we put an amp meter on the ground we had 160 amps, phases where around 250 amps, and only 4 amps on neutral. We had utility company come who confirmed high voltage was a problem from their substation and they corrected it. The amperage and the heat went down significantly but didn't go away currently values voltage 278 278 277, amperage 54 63 50, amperage on ground 41, amperage on neutral 4 amps. So when we started looking into the UPS possible being the issue we came across this see pics below. I have also attached the manual for the UPS.
Do you think this is where we are getting our imbalance from?
Answer to some questions you may have
Building transformer is Wye to Wye
CAT scan is straight 3 phase 480V that requires a Isolated ground same size as feeders and a redundant isolated ground #4
AT PANEL Isolated ground is bounded with bug to panel and redundant to ground bar
AT UPS Input isolated ground is not on grounding electrode but to the frame
AT UPS Input redundant ground is on output neutral bar but bonded to frame with that copper plate you see in pic
AT UPS Output isolated ground and redundant are also on Output neutral bar with Input redundant ground
Yes shutting down CAT scan would confirm that is where the imbalance is from but trying to find a time we can put it out of service is not easy