All of a sudden, a 2 pole 20 amp 208 volt breaker started tripping on an LED circuit. When I troubleshot the circuit I found out that one leg was drawing 49 amps and the other leg was barely drawing anything at all. I also went through each light and disconnected that light from the circuit one at a time and the breaker still tripped when I did this on all of the lights. This circuit has been on constantly for around a year-and-a-half and hasn't had a problem and all of a sudden this started happening. Was wondering if anyone had any knowledge on this issue or has dealt with this in the past.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
170713-1041 EDT

Your question is not real clear.

You are implying a single two wire circuit supplying a parallel bank of LED lights supplied from a 208 voltage source.

208 implies a 3 phase wye source with 3 hot wires relative to ground, and one neutral with about 0 V to ground.

At 208 V how much current does one LED draw?
How many LEDs on this circuit?

What are your three phase voltages to neutral?
What is the neutral to ground voltage? Use a screwdriver in the earth somewhere and a high impedance meter.

My guess is that you have a resistive short to ground or neutral on the high current leg that is drawing a good portion of your high current. More information would have been useful.

.
 