brycenesbitt
- United States
There was more high drama at the NFPA.
The standards council rejected the vote at the technical meeting regarding 14 AWG Copper Clad Aluminum wiring.
The accusations and bad faith going back and forth were dramatic: accusations of vote rigging, test rigging, and apparently personal litigation against individual members of the CMP. It featured vendors who sell one type of product who passionately spoke about why the other guy's product was bad.
Wow. Someone needs to write a tela-novella or at least a podcast.
Allied Tube v. Indian Head, Inc. | 486 U.S. 492 (1988) was invoked multiple times.
Pretty high drama.
The SC dismissed all that, but focused on process:
And while rejecting the claim the vote was rigged at the Technical Meeting, did disregard that same vote:
So if you were in the room, that historic moment when CCA was approved, did happen.
The new rule is:
Thus you will be able to run LED lighting circuits using the lighter weight wire, on 10A breakers.
Will 16 AWG CCA and 5A breakers be next?
Or just energy harvesting from WiFi signals for lighting?
Read all about it next year at https://www.nfpa.org/sc2026
Or today at https://www.nfpa.org/sc2025
Pretty high drama.
During the present revision cycle, CMP 6 reached consensus on the inclusion of 14 AWG CCA and 16
AWG at both the First and Second Draft stages of the NFPA standards development process. The record
reflects that CMP 6 reviewed multiple reports submitted, including the FPRF Report. There were no
conflicting data or test reports submitted to oppose the research CMP 6 relied upon to add 14 AWG CCA
to Section 310.5(A).
In the view of the Council, this appeal does present a clear and substantial basis upon
which to overturn the results yielded by the NFPA standards development process. Accordingly, the
Council has voted to uphold the appeal. The effect of this action is that NFPA 70, National Electrical
Code, will include Section 310.5(A) as amended by SR 8471
The new rule is:
310.3(A) Minimum Size of Conductors.
The minimum size of conductors for voltage ratings up to and including 2000 volts shall be 16 AWG copper, 14 AWG copper-clad aluminum, or 12 AWG aluminum, except as permitted elsewhere in this code
210.24 Minimum for 10A breakers is changed to match.