Hello all,
I received the following from the electric utility. The system consists of multiple 250 kVA to 500 kVA transformer banks tied together with 208 V, 3ph secondaries.
"The % X/R ratio for the power line is 2.87. {Electric Utility's} contribution to a fault at the customer’s service point is 58,173 Amps at 208V or 19.65MVA three phase symmetrical. The ultimate fault could be as high as 80MVA in the future."
While I don't get the exact same results 19,650 kVA / (208 * sqrt(3) = 54,583 kA, it is similar to what was received in the letter.
At 80 MVA it would be 222.22 kA = 80,000 kVA / (208 * sqrt(3))
Is there service equipment sized to handle >200 kA? Or is the better path to install equipment rated 200 kA and inform the Owner of the decision. I've found Class L fuses rated up to 300 kA but am unable to find enclosures to put them in.
I received the following from the electric utility. The system consists of multiple 250 kVA to 500 kVA transformer banks tied together with 208 V, 3ph secondaries.
"The % X/R ratio for the power line is 2.87. {Electric Utility's} contribution to a fault at the customer’s service point is 58,173 Amps at 208V or 19.65MVA three phase symmetrical. The ultimate fault could be as high as 80MVA in the future."
While I don't get the exact same results 19,650 kVA / (208 * sqrt(3) = 54,583 kA, it is similar to what was received in the letter.
At 80 MVA it would be 222.22 kA = 80,000 kVA / (208 * sqrt(3))
Is there service equipment sized to handle >200 kA? Or is the better path to install equipment rated 200 kA and inform the Owner of the decision. I've found Class L fuses rated up to 300 kA but am unable to find enclosures to put them in.