kcs47
Member
- Location
- Kingsbury, NY
- Occupation
- Electrical Controls Technician
We have a building at our converting manufacturing site that has had some weird low voltage signal anomalies over the past 1-2 years. It was a new building 24 years ago with similar VFD equipment but only recently started surfacing new problems. It is loaded with 480V VFD's and we upgraded from incandescent bulbs to LED's within the past 5 years. A year or so ago we started getting DH+ plus faults on the associated hardware. This past year we started getting into encoder loss faults on our 1336 Force Drives and Position error faults on our Servo Axis Cards. Last week we finally found something worth investigating a bit further:
Here is a summary of the checks we did on Lines 125 and 124 yesterday (Thursday 6 Jun 2024) and the results:
First, we looked at Line 125. We checked the Voltage and resistance between +24Vdc, Common, and Ground, as measured at the power supplies. The measurements were as expected, which are:
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0V, <10 Ohms
Next, we checked Line 125 several panels away from the Power Supplies, which displayed some Stray Voltage showing up in the Common or Ground of the System.
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0.7V, > 1kOhm
We obtained a long cable and used it to confirm that there was a good connection in the ground system between panels. We connected the cable to a ground in a remote panel, and then repeated the measurements to the Common and +24Vdc at the Power Supply. The measurements were the same.
Then we checked Line 124. Checking the Voltage and Resistance at the power supplies we measured the correct results:
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0V, <10 Ohms
Checking multiple panels further away from the Power Supplies, we saw similar stray voltages showing up just like Line 125:
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0.5V, > 1kOhm
Also note that the incidence of voltage was *not* higher the further we got from the Power Supplies. The gradient on Line 124 appeared to be going the other way, as if the leakage was coming close to the Power Supply panels, and settling out to 0 leakage the further we got from it.
We plan to take our Fluke 225C Scope Meter out and determine what may be on the grounding system causing the impedance on our grounding system. Any words of advice is much appreciated. I am a decent controls technician but have limited experience with Noise, Harmonics, power quality, etc.
Thank you,
-Tyler
Here is a summary of the checks we did on Lines 125 and 124 yesterday (Thursday 6 Jun 2024) and the results:
First, we looked at Line 125. We checked the Voltage and resistance between +24Vdc, Common, and Ground, as measured at the power supplies. The measurements were as expected, which are:
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0V, <10 Ohms
Next, we checked Line 125 several panels away from the Power Supplies, which displayed some Stray Voltage showing up in the Common or Ground of the System.
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0.7V, > 1kOhm
We obtained a long cable and used it to confirm that there was a good connection in the ground system between panels. We connected the cable to a ground in a remote panel, and then repeated the measurements to the Common and +24Vdc at the Power Supply. The measurements were the same.
Then we checked Line 124. Checking the Voltage and Resistance at the power supplies we measured the correct results:
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0V, <10 Ohms
Checking multiple panels further away from the Power Supplies, we saw similar stray voltages showing up just like Line 125:
+24Vdc to Common : 24V
+24Vdc to Ground : 24V
Common to Ground : 0.5V, > 1kOhm
Also note that the incidence of voltage was *not* higher the further we got from the Power Supplies. The gradient on Line 124 appeared to be going the other way, as if the leakage was coming close to the Power Supply panels, and settling out to 0 leakage the further we got from it.
We plan to take our Fluke 225C Scope Meter out and determine what may be on the grounding system causing the impedance on our grounding system. Any words of advice is much appreciated. I am a decent controls technician but have limited experience with Noise, Harmonics, power quality, etc.
Thank you,
-Tyler