Miguel c
Member
- Location
- Barranquilla colombia
- Occupation
- Bilingual agent
Suppose we have a line at 120 V 200 ft long 3 AWG wire, impedance 0.05 ohms
Circuit breaker lets say is a 200 A one
Now there is a grount fault and we have a 14 AWG EGC wire, 200 ft long, (violation) the EGC's impedance is 0.6344 ohmios, therefore the graunt fault current is 175 A, hence the breaker does not trip, now the metal parts are energized. Would that provide the potential for electric shock taking into account we still have an effective ground fault current path and the neutral is bonded to ground?
Circuit breaker lets say is a 200 A one
Now there is a grount fault and we have a 14 AWG EGC wire, 200 ft long, (violation) the EGC's impedance is 0.6344 ohmios, therefore the graunt fault current is 175 A, hence the breaker does not trip, now the metal parts are energized. Would that provide the potential for electric shock taking into account we still have an effective ground fault current path and the neutral is bonded to ground?