I have a customer that wants to plug in a 15 amp treadmill on a 15 amp circuit. She said the manufacturer suggests upgrading to a "high inrush breaker QO120HM. I can't do that can I??
Why do you question it?I have a customer that wants to plug in a 15 amp treadmill on a 15 amp circuit. She said the manufacturer suggests upgrading to a "high inrush breaker QO120HM. I can't do that can I??
I have a customer that wants to plug in a 15 amp treadmill on a 15 amp circuit. She said the manufacturer suggests upgrading to a "high inrush breaker QO120HM. I can't do that can I??
The standard Square D QO 15 and 20A breakers trip faster than most of those from the rest of the industry. This is why Square D makes some for high magnetic inrush circuits (16-26X).There are fast- and slow-blow fuses, but breaker characteristcs are pretty much identical at this level, and adjustable at much larger sizes.
When you say 15 amp treadmill do you mean that it can be used on a 15 amp circuit or that it draws 15 amps?
If I assume it is actually a 12 amp treadmill then:
If they were to suggest a QO115HM that should work.
I believe they are recommending the "high magnetic" because it will better tolerate the high inrush currents of the treadmill.
The high magnetic will allow a higher amplitude of current for the same amount of time as the standard breaker.
We installed QOHM all the time for nuisance trip issues due to inrush.
This lady did not give me much information and only called to get a quote on replacing a 15 amp breaker with a 20 amp HM breaker. I've never used a HM breaker before only fuses. I told her if the treadmill pulled that much she would need a 20 amp circuit. She refused to believe me and said she would call somebody else.
On another job I am have nuisance tripping on a 15 amp arcfault Square D breaker. It's a condo that is wired in conduit, metal boxes, and MC and was wired when just the bedrooms were on the arcfault. Have you ever had a problem with a plug strip with surge protection tripping an arcfault?
Have you ever had a problem with a plug strip with surge protection tripping an arcfault?
Some of the treadmills do come with a 20A plug on them, doesn't mean that is what they draw, but some are made with a 5-20P