bill@usps06492
Member
- Location
- Connecticut
I've been working in this older commercial building that has 120/240-208v 3ph delta service with a single throw 400a main disconnect switch. The voltages are 240v between phase ab,bc,& ac, and from either a or b phase it's 120v to the neutral & ground. On phase c it's 208 to neutral & ground. Are there any special requirements for bonding grounds and neutrals in these systems? There are panels in this facility that have the neutral and ground landed on an isolated neutral bar, and in the same panel there is a ground bar that is isolated from the panel and not bonded to the neutral. It has always been my understanding that once your out of the main service disconnect the neutral is isolated from the panel and the ground. They are only bonded together at the service disconnecting point. I haven't found anything in the NEC to lead me to believe that a delta system should be bonded and grounded any differnt. My concern is that if I start to correct these, can something happen with the system voltage? Thanks Bill