High Leg Conductor

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
load

load

The simple answer would be "like any other conductor" ie: determine what equipment is connected to the high leg, however, if you are dealing with a main breaker service, the size of condcutor on all phases will be determined by the load AND the service breaker size.
 
Status
Not open for further replies.
Top