alblock
Member
- Location
- NC, TN, SC
- Occupation
- Industrial Electrician
Wiring in a 3 phase 220v cnc machine. Transformer will be right next to cnc using EMT.
We have 480 3 phase.
Normally use wye secondary or use ungrounded.
Manufacturer states it has to be grounded and can use corner or center on delta, or neutral if wye.
Had a delta delta transformer with X4 terminal.
Secondary side of a wye transformer we would bond X0, EGC, SBJ, and run Grounding Electrode to building steel.
Does anything change with this high-leg delta?
I think just treat it the same as a wye and bond X4, EGC, SBJ, and run Grounding Electrode to building steel.
Thank You.