I'll spare the details on how this happened except to say that the utility and my journeyman had a communication gap...original high leg wire was moved by the utility during a reconnect call and put into currently-accepted location (right side of meter). My JM put back with assumption that the high leg was going to stay in the middle position where it originally was...I figured my team's fault really for not checking the voltage with a meter immediately and quickly recognizing the error and miscommunication.
So you might imagine what happened. The stove in this old commercial building didn't get its 240 split phase but a 120 / 208 V combo - burnt. Numerous ballasted lights burnt out. All this replaced by me.
My question for all is should the circuit breakers in the main panel be replaced since the leg received high voltage stinger leg and not the 120V. Will / could a breaker be damaged and is it good practice to replace the 20 or so breakers in the panel out of an abundance of caution?
I have not checked the labeling of each breaker but I suspect they are 120/240 dual pole breakers and the single poles (of which there are many) are 120V rated.
Thanks.:?
So you might imagine what happened. The stove in this old commercial building didn't get its 240 split phase but a 120 / 208 V combo - burnt. Numerous ballasted lights burnt out. All this replaced by me.
My question for all is should the circuit breakers in the main panel be replaced since the leg received high voltage stinger leg and not the 120V. Will / could a breaker be damaged and is it good practice to replace the 20 or so breakers in the panel out of an abundance of caution?
I have not checked the labeling of each breaker but I suspect they are 120/240 dual pole breakers and the single poles (of which there are many) are 120V rated.