High leg marking

Merry Christmas
Status
Not open for further replies.

nizak

Senior Member
What is the correct color identification for the high leg of a 120/240 V Delta 3 phase system?

Orange?
Purple?

Thanks
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
110.15 High-Leg Marking.


On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded, only the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is orange in color or by other effective means. Such identification shall be placed at each point on the system where a connection is made if the grounded conductor is also present.

Orange markings is most popular, but other effective means can be about anything.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Check out 110.15

110.15 High-Leg Marking. On a 4-wire, delta-connected
system where the midpoint of one phase winding is grounded,
only the conductor or busbar having the higher phase voltage
to ground shall be durably and permanently marked by an
outer fnish that is orange in color or by other effective means.
Such identifcation shall be placed at each point on the system
where a connection is made if the grounded conductor is also
present.

Chris
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
110.15 is the requirement from the NEC, which is what WE must follow. The use of other colors, like purple or red or (in one case I saw) yellow, is what the UTILITY supplies on the incoming service. THEY do not have to follow the NEC. So here in SF, where I too have come across the purple phase tape, I STILL HAD TO USE ORANGE after the service meter. That's the rule. Pay no attention to what the utility does on their side, it doesn't matter to you.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
110.15 is the requirement from the NEC, which is what WE must follow. The use of other colors, like purple or red or (in one case I saw) yellow, is what the UTILITY supplies on the incoming service. THEY do not have to follow the NEC. So here in SF, where I too have come across the purple phase tape, I STILL HAD TO USE ORANGE after the service meter. That's the rule. Pay no attention to what the utility does on their side, it doesn't matter to you.

I have not looked at the SF electrical code recently but it has always required purple instead of orange for marking the high leg.

Edited to add copy of SF requirements.
On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded, only the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is purple [ß] in color or by other effective means. Such identification shall be placed at each point on the system where a connection is made if the grounded conductor is also present. Identification of ungrounded feeder conductors shall comply with Section 210-5(C).
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
110.15 is the requirement from the NEC, which is what WE must follow.
But it then immediately says or by other effective means - which leaves it wide open. Like I said, orange is most common, but is not the only way. They don't even limit the use of orange to high leg identification like they limit white/gray to grounded conductors or green to grounding conductors. Is pretty common to use orange as identification of one leg of 480/277 wye systems.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
But it then immediately says or by other effective means - which leaves it wide open. Like I said, orange is most common, but is not the only way. They don't even limit the use of orange to high leg identification like they limit white/gray to grounded conductors or green to grounding conductors. Is pretty common to use orange as identification of one leg of 480/277 wye systems.

By saying other effective means, does it mean other effective colors or other effective means like (tags)
 

Carultch

Senior Member
Location
Massachusetts
I have not looked at the SF electrical code recently but it has always required purple instead of orange for marking the high leg.

Edited to add copy of SF requirements.
On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded, only the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is purple [ß] in color or by other effective means. Such identification shall be placed at each point on the system where a connection is made if the grounded conductor is also present. Identification of ungrounded feeder conductors shall comply with Section 210-5(C).

So does this mean that in SF, you have to strip it orange and purple to comply with both the local and national code?
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
So does this mean that in SF, you have to strip it orange and purple to comply with both the local and national code?
I think they have their own code - is mostly based off NEC content though, this is just one thing that is different from NEC.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
By saying other effective means, does it mean other effective colors or other effective means like (tags)
IMO it is wide open. Could use any color but white, gray and green because those are reserved for specific use, but if you use another color you may need to indicate somehow what that color represents. If you use orange you shouldn't have to indicate what it means.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Either will suffice. But if non-standard, the meaning of color or any non readable tags should be posted in the way that system voltage and phase is posted for multi-system buildings.

mobile
 

Carultch

Senior Member
Location
Massachusetts
It means what it says: permanently marked by an outer fnish that is orange in color or by other effective means.

The national industry norm is to mark it orange, or use orange wire for #6 and smaller. The context of other wire colors usually distinguishes it from the B-phase in a 480V system. SF has a local requirement for marking it violet.


If you deviate from the industry norm, it needs to be explained on the equipment itself. Textual wire tags, permanent equipment cover labels, or anything else. Anything you can do to make the high leg as vivid as possible is encouraged.
 