Beside the marking on the wire, is it required somewhere in the NEC to mark the panels with the word HIGH LEG as well?

Yes and the wording is specific.

408.3(F)(1) High-Leg Identification. A switchboard, switchgear,
or panelboard containing a 4-wire, delta-connected system
where the midpoint of one phase winding is grounded shall
be legibly and permanently field marked as follows:
“Caution _____ Phase Has _____ Volts to Ground”
 
Yes and the wording is specific.

408.3(F)(1) High-Leg Identification. A switchboard, switchgear,
or panelboard containing a 4-wire, delta-connected system
where the midpoint of one phase winding is grounded shall
be legibly and permanently field marked as follows:
“Caution _____ Phase Has _____ Volts to Ground”

It has no instruction to fill appropriate values in the blanks:D
 