High Leg Power Calculation

Status
Not open for further replies.

Tank11

Member
Location
CO
Hello,
I've run across a panel that is 240/120-volt with a high "B" leg. The main breaker is 200-amps.

How do I calculate the total power available on this panel? Is it 240*Sqrt(3)*200? Or is it 240*200?

Thank you
 
Neither. The total power available will depend on the mix of 120/20 and three phase loads as well as whether the service transformers are same size.
If all you are concerned about is the load the OCPD will allow, the max would be with fully balanced three phase after adding in the 120/240 load.
Your first number.
If the bulk of the load is A to ,C, then the second number.
 
Hello,
I've run across a panel that is 240/120-volt with a high "B" leg. The main breaker is 200-amps.

How do I calculate the total power available on this panel? Is it 240*Sqrt(3)*200? Or is it 240*200?

Thank you
3 phase kVA would be A x V x 1.732, your 3 phase voltage is 240V. Don't get hung up on the High leg.

If what you want to know is how much SINGLE PHASE power you have available on that system, that's a different matter. You can't calculate that, you have to read it. Depending on the configuration of the transformer(s) feeding this system, there will be restrictions on the amount of 120V power you can use from it. That should be in the description of your service from the PoCo. Some are limited to just 5% of the transformer rating for example.
 