Are you saying that all phases have 120 to ground?readings
A to ground 120
B to " "
c to ground " (high leg)
A to C 0
A to B 240
B TO C 240
lost high leg?
Forget the readings to ground.readings
A to ground 120
B to " "
c to ground " (high leg)
A to C 0
A to B 240
B TO C 240
lost high leg?
Couldn't A or C be not powered and the OP is reading through a load? Wouldn't exactly be a "short".Forget the readings to ground.
A to C 0
A to B 240
B TO C 240
A is shorted to C
Are you saying that all phases have 120 to ground?
correctCouldn't A or C be not powered and the OP is reading through a load? Wouldn't exactly be a "short".
That was my assessment A and C together but what i find puzzling is this is a apartment building the only 3phase is fire pump moters and elevatorreadings
A to ground 120
B to " "
c to ground " (high leg)
A to C 0
A to B 240
B TO C 240
lost high leg?
any way waiting on power companyThat was my assessment A and C together but what i find puzzling is this is a apartment building the only 3phase is fire pump moters and elevator
elevator still working with the same readings
There might be an open delta to create the high leg, but in this case there's zero volts across the primary of the transformer supplying the high leg. This could be caused by a ground fault on the primary or the feeder to it, or by some other problem on the utility side. With zero volts across the primary there will be zero volts across the secondary, and so A will look like it's shorted to C.readings
A to ground 120
B to " "
c to ground " (high leg)
A to C 0
A to B 240
B TO C 240
lost high leg?
A and C would be coming from the same transformer, right? The 2nd transformer would supply the high leg. If the second transformer lost the primary, wouldn't A and C still be working properly? I must not be understanding what you are saying.There might be an open delta to create the high leg, but in this case there's zero volts across the primary of the transformer supplying the high leg. This could be caused by a ground fault on the primary or the feeder to it, or by some other problem on the utility side. With zero volts across the primary there will be zero volts across the secondary, and so A will look like it's shorted to C.
I hope you let us know what you find.any way waiting on power company
readings
A to ground 120
B to " "
c to ground " (high leg)
A to C 0
A to B 240
B TO C 240
lost high leg?
A and C would be coming from the same transformer, right? The 2nd transformer would supply the high leg. If the second transformer lost the primary, wouldn't A and C still be working properly? I must not be understanding what you are saying.