Electric-D
Member
what exactly is a high leg?
brian john said:The high leg delta service was used in older industrial applications (In my expierence) where they had 3 phase loads and very little 120 loads. This connection gives you 120 VAC for lighting and utilization outlets.
Normally one would avoid the 208 to neutral connections as 120 VAC loads seem to fry at this voltage.
catchtwentytwo said:He tried to argue by claiming that you could "get away with it" by merely blanking off any unused high-leg pole positions and marking them "do not use".
Bob,iwire said:I believe that would be NEC compliant
As far as I know you simply do not use the high leg spaces and you are not required to mark them.
catchtwentytwo said:I should have clarified that by stating our POCO (and most local AHJs where the "high-leg" is used ) wanted the single-phase panel. I'm told too many cases of someone eventually using the "available" single-phase space without realizing the consequences drove this.
I think the issue is that there seems to be no single pole breakers available for the types of panels that are typically used on a high leg system that are rated for 208. If there were, it would be compliant, in my opinion. You'll still see this from time to time anyhow. People say that the high leg voltage can vary wildly, but that has not been my experience at all.brian john said:Single phase 208 VAC motors would operate off this voltage, but I believe this would be a NEC violation? Just curious or truthfully to lazy to go the the bathroom to retrieve Code book.
Would this be the transformer from which "B" phase is derived? I'd guess it's smaller because unlike the other two phases, it doesn't usually supply any single phase loads?catchtwentytwo said:You can spot an installation using because one of the three pole mounted XMFRs is usually physically smaller.
Builder said:On a open delta system, is there a sine wave produced on the open side of the system, where the missing transformer is?
roger said:Torcho, the 208 high leg to neutral is an unusable voltage of a 240/120v grounded Delta system. It is simply an unavoidable voltage that is present in the system.
Roger
K2500 said:What makes this voltage unusable? I don't understand. Is it not practical, or not possible?
K2500 said:What makes this voltage unusable? I don't understand. Is it not practical, or not possible?