I ran across a situation where a compressor was moved, and they wanted me to rerun the wires and rehook up the unit, What i found was that i had 219 volts on one phase coming in and 120 on the other, The unit calls for 230 volts single phase and is 7.5 h.p. Is there a problem with this high leg feeding this air compressor? Thank you so very much I have learned a great deal from this forum.
 

butch

Member
Re: high leg

Yes Sir I did measure both voltages to ground and i also measured across phases with a 229 volt reading does this seen appropreiate. Thank you so much Tom Ill have to go back today and do soom final readings for the customer. Again thanks so much !!!!!!
 

russ

Senior Member
Location
Burbank IL
Re: high leg

This is normal for 3 phase 240. the 240 motor doesn't care that one of the phases is higher to ground. The only important thing is that you get 240 between phases. If there were 110 volt controls tapped off the motor feed that could cause a problem , but with this install you don't have that.

[ January 11, 2004, 09:35 AM: Message edited by: russ ]
 

butch

Member
Re: high leg

Thanks again my fellow professionals the rreason I brought this up was that previously they have had some poblems with the windings on this unit. your help and support help me look more professional We all know 3 heads are better than one. Thanks so much !!!!!!!!!!!!!!!!!!!!!!!!! Anad may you have a wonderful new year.
 