I am getting 400V and 600V on L-G and L-N readings on the secondary of a 240V/120V transformer.
We have an outdoor 4.16kV stand alone breaker cubicle. Inside this cubicle there is a 4.16kV to 240/120V transformer to supply control power to the breaker relays and heaters that are in the cubicle. We powered everything down today to put high temp wire on heaters and when we turned power back on we noticed a relay smoking. This is a realy which we just had repaired sometime back and was damaged for some reason.
We took voltage measurements and saw that we has 240V on the two hot wires coming of the secondary of the transformer however we read 400V from one leg to ground and 600V from the other leg to ground. The tranformer neutral is center tapped and tied to ground. These readings do not make sense to me. Even if something was grounded on the secondary of the transformer I would not expect to see more than 240V for a L-G reading. How in the world would I be reading 600V?
X2 and X3 of the transformer are tied together and then brought out and bonded to the cubicle casing as a ground reference. This same point is used to tie all of the neutrals in from the various relays and heaters. This is also giving us L-N voltages of 400V and 600V. I am afraid that with these L-N voltages across these electronics that I wil fry the relays.
Does anyone know what could be happening?
We have an outdoor 4.16kV stand alone breaker cubicle. Inside this cubicle there is a 4.16kV to 240/120V transformer to supply control power to the breaker relays and heaters that are in the cubicle. We powered everything down today to put high temp wire on heaters and when we turned power back on we noticed a relay smoking. This is a realy which we just had repaired sometime back and was damaged for some reason.
We took voltage measurements and saw that we has 240V on the two hot wires coming of the secondary of the transformer however we read 400V from one leg to ground and 600V from the other leg to ground. The tranformer neutral is center tapped and tied to ground. These readings do not make sense to me. Even if something was grounded on the secondary of the transformer I would not expect to see more than 240V for a L-G reading. How in the world would I be reading 600V?
X2 and X3 of the transformer are tied together and then brought out and bonded to the cubicle casing as a ground reference. This same point is used to tie all of the neutrals in from the various relays and heaters. This is also giving us L-N voltages of 400V and 600V. I am afraid that with these L-N voltages across these electronics that I wil fry the relays.
Does anyone know what could be happening?