We have a 480 wye connected secondary feeding a 2000A bus. The system is using a Post Glover HRG. We have 6 parallel feeders running in PVC conduits in a concrete duct bank.I am having trouble determining what is required to be in the conduit with the feeder cables and how to size them. Does 250.122 even apply? Can these feeder cables be run with just the 3 phase power and no ground in each conduit? 250.36 (D) allows for the Neutral point to grounding Impedance Conductors to be installed in a separate raceway. Does this imply that the phase conductors are the only conductors in that raceway?
Why would we size the EGC using 250.122 if ground current is limited to 5-10A?
Any help understanding this would be greatly appreciated!
Thanks!
Why would we size the EGC using 250.122 if ground current is limited to 5-10A?
Any help understanding this would be greatly appreciated!
Thanks!