Hello, this is my first time posting a topic so I hope this is in the correct spot. I was called in to a facility to look at 2 hoist drives on cranes that went out. Upon metering the incoming power I found that b phase was grounded. I went to maintance and told them what I found. We went to the main gear room of the plant and the ground resistor was extremely hot. I told them that it needed fixed before we blew up 30,000 in new drives.
The service is a 4,000 amp 480 volt 3 phase 3 wire system. On their 1 line diagram it shows the 25kv feed from the utility through metering service disconnect then feeding the transformers. It shows a delta primary and a wye secondary but only 3 wire system. I am not very familiar with this type of distrubution. Maintance did turn off as many loads as they could but could not clear the fault.
Also the ground indicator lights have been unhooked from the system, I hate to call osha but they not wanting to fix it means that I can not fix the cranes and over the 4 hours I was there the fault got worse. It want from 20 volts to ground to 35 volts to ground.
Can anybody recommend a good reference to learn more about this kind of system. Also would you notify osha or somebody else?
Sent from my SM-N900V using Tapatalk
The service is a 4,000 amp 480 volt 3 phase 3 wire system. On their 1 line diagram it shows the 25kv feed from the utility through metering service disconnect then feeding the transformers. It shows a delta primary and a wye secondary but only 3 wire system. I am not very familiar with this type of distrubution. Maintance did turn off as many loads as they could but could not clear the fault.
Also the ground indicator lights have been unhooked from the system, I hate to call osha but they not wanting to fix it means that I can not fix the cranes and over the 4 hours I was there the fault got worse. It want from 20 volts to ground to 35 volts to ground.
Can anybody recommend a good reference to learn more about this kind of system. Also would you notify osha or somebody else?