Re: High Resistance Grounding
danilo:
Buenas noches, Yo soy Pablo.
I am not a big fan of High-Resistance grounding systems UNLESS you ABSOLUTELY must have continuity of power. Since you said that continuity of power is the top priority, here are my pros and cons:
PROS:
Power stays on during first ground fault.
Somewhat reduced arc-flash hazard.
Reduces damage to equipment compared
to solidly grounded systems.
CONS:
No ground reference for test equipment.
Arc-flash hazard is still present from phase
to phase, so protective clothing is still
required (at least in the U.S.)
HRG systems require greater training and
troubleshooting skills on the part of your
electrical maintenance personnel. (No more
quick fault locating.)
HRG systems expose electricians to increased shock
hazards (in my opinion) because all troubleshooting must be done with the equipment energized.
HRG systems cannot serve line-to-neutral
loads. Isolation transformers must be used
for line-to-neutral circuits.
Ground detectors are required on the HRG
system, electricians must respond QUICKLY to
clear any faults.
Faults are harder to find unless you install a
tracing circuit and/or equip your electricians with
flexible-current probes and meters for use with
pulsers, as RCWILSON has pointed out.
HRG systems do not fix your ground-fault
problems, they only buy you a little time to
find the problem, as RON has pointed out.
But hey at least you are still running.
HRG is limited to systems operating from
380 V up to 5 kV. Above 5 kV, more careful
evaluation is required due to the probability
of increased capacitive charging currents on
the system.
In conclusion:
If you must have continuity of power, and your
system is 380 V to 5 kV, then HRG is probably
your only solution. But I would question you as
to why your selective co-ordination is not keeping your ATS's from tripping on [other] ground faults? Sounds like you might have a design problem and this vendor is trying to sell you a HRG system so he can make money????