RRonke
- Lincoln,NE
I get resistance readings from .1 ohm to 98 ohms when testing neutral to equipment ground in a customer's house. I was testing because his 4' wide curved plasma arc
TV and two plug in surge protectors were ruined when plugged into the recept. behind the TV. Found hot wire fell out of receptacle when I removed it (a stabbed in connection). I wanted to make sure equipment ground was good but neutral to ground tested at 47 ohms. But when a extension cord was used to test to a "good" ground that tested at .1 ohm to neutral, all receptacles and this one tested at .1 ohm. He's asking me to make sure his replacement TV won't go up in smoke. I think that as long as the equipment ground is good the surge protector should have a place to dump to and the loose hot wire could have caused problems but I did not see any signs of arcing on the hot wire that was not connected good. I don't think the 47 ohms reading should be a worry but I'd like some opinions. I have never run into this in 22 years of wiring maybe because I have never tested a bunch of receptacles like this.