Can high temperature wire be run inside LTFM and EMT? ,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,Thank you
Then yes you can.FEP yes
May just be my foggy brain.. is LTFM the same a s Art 350 LFMC ??
If so, would 350.12 not come into play ?
: 350.12 Uses Not Permitted. LFMC shall not be used as follows: (2) Where any combination of ambient and conductor temperature produces an operating temperature in excess of that for which the material is approved