NEC more or less doesn't allow circuits in spaces for environmental air unless they are for components within that space, exceptions for spaces above ceilings and under raised floors.
Otherwise within the furnace itself - mostly need to refer to listing requirements more so then NEC. If it isn't for something in that furnace it probably doesn't belong there for certain.
Otherwise the blower motor itself is usually powered by conductors inside the space you question, but it is listed that way.
The hvac company blocked off the knock out where the main power would enter the furnace. Now I would have to make my own hole in the blower compartment just to be able to get to the 60 amp disconnect located in the furnace.
That could be a problem if that 60A feed is powering a heating element or a compressor while the only wiring normally in the blower compartment is for the fan only.
Many furnaces I have seen have the main incoming power feed is a separate compartment with its own entry point(s).
If those are inaccessible there is no way you can comply with the manufacturers instructions and the UL listing conditions.
So regardless of the practical safety of your planned route an AHJ would be justified in rejecting it.
mobile
I would run the wiring on the outside of the air handler.
I agree. Why not run flex across the top and down the right side?
Definitely a bad installation by the HVAC guys.
Is there any way you could have come directly into the left side of the lower compartment instead of going through the upper (blower) compartment?
mobile
No. If you look at the picture you can see it's completely blocked by other wiring, metal plates and circuit boards.
In that case, I would run flexible metal conduit thought the blower compartment and seal it off accordingly with duct sealant.
Why the FMC? Is the wire subject to damage in there?
No, but that's how I would have done it.
Because he can't bend pipeWhy the FMC? Is the wire subject to damage in there?
Because he can't bend pipe![]()