B Big Guns Member Jul 5, 2012 #1 Can you run 120 volts through same conduit as speaker wires with no interferance if all the wire ran in conduit is THHN 600 volt rated or does the speaker wire have to be speaker wire in seperate conduit.
Can you run 120 volts through same conduit as speaker wires with no interferance if all the wire ran in conduit is THHN 600 volt rated or does the speaker wire have to be speaker wire in seperate conduit.
kwired Electron manager Location NE Nebraska Occupation EC Jul 5, 2012 #2 Can it be done with no intereference - likely. Can it be done and comply with NEC - likely not. Chances are the speaker circuit is a power limited circuit and not allowed to be run with power circuits.
Can it be done with no intereference - likely. Can it be done and comply with NEC - likely not. Chances are the speaker circuit is a power limited circuit and not allowed to be run with power circuits.
N nhfire77 Senior Member Location NH Jul 5, 2012 #3 The output on the amplifier would need to be class 1 but the instructions probably tell you it's not permissible.
The output on the amplifier would need to be class 1 but the instructions probably tell you it's not permissible.