I have got a situation in a plant where VFD's have been tripping off due to high voltage. 521 volts was measured at the VFD's. The VFD's were originally set at 460 volt and the high limit raised up to 480 volt with 10% allowance. We are having the utility change the taps on the transformer down to 500V at the secondary of the transformer. (I am not sure why we cannot reduce down to the 480V and have to ask the utility).
Question: Is there a negative effect of running motors, compressors, HID ballasts, UPS's on a voltage +5%?
Question: Is there a negative effect of running motors, compressors, HID ballasts, UPS's on a voltage +5%?