In my job as an Electrical Technician I have come upon a serious problem; which I hope this forum might be able to help me with.
A heat tracing hot wire had a simple ground failure, which cut out a 20A breaker along with a 100A main breaker in a 480V installation, probably because of a very high short circuit currant (more than 3500A).
Under re-closing both the 20A and 100A breakers a short-circuit happened again, and this time not only are the two breakers cut out, but the whole high-voltage circuit (4,160V) is cut out on a HV earth failure.
This makes no sense to me - how can a high-voltage circuit see a low-voltage ground failure?
It is an ordinary d-y transformer and the high-voltage circuit is been checked out.
The relay is a Westinghouse type and calibrated every 2 years.
What can the reason be for the above failure?
The location is under Artic conditions and the grounding/bounding system, on witch the 480V neutral point is mounted, is connected to a copper plate placed in seawater.
I will be patiently waiting in anticipation of hearing from you.
Best regards,
A heat tracing hot wire had a simple ground failure, which cut out a 20A breaker along with a 100A main breaker in a 480V installation, probably because of a very high short circuit currant (more than 3500A).
Under re-closing both the 20A and 100A breakers a short-circuit happened again, and this time not only are the two breakers cut out, but the whole high-voltage circuit (4,160V) is cut out on a HV earth failure.
This makes no sense to me - how can a high-voltage circuit see a low-voltage ground failure?
It is an ordinary d-y transformer and the high-voltage circuit is been checked out.
The relay is a Westinghouse type and calibrated every 2 years.
What can the reason be for the above failure?
The location is under Artic conditions and the grounding/bounding system, on witch the 480V neutral point is mounted, is connected to a copper plate placed in seawater.
I will be patiently waiting in anticipation of hearing from you.