Hi All
I am new to this forum and if possible I would like to get some advice on the following please.
I attended a fault on a UV unit that has a 4-20 ma output to a logger which in turn is connected to other devices giving analogue and digital signals all of which have a common negative on breakout box of logger.
A fitter changing a reed switch on a flow meter and reported that he received a substantial shock when he was replacing the reed switch which normally works at 3.9 v DC. I measured voltage on pair of wires to reed switch and recorded 3.9V DC but I did notice that my volt tick was showing high AC Voltage present, I then measured from each leg of wire to reed switch and recorded 125 Volts AC to main earth and neutral bar on distribution board.
I eventually traced the 125 V AC to 4-20 ma output on UV unit and found it had back fed via logger breakout box(common negatives) and in turn was present at all devices connected to logger. I thought at first this might be a floating/induced voltage but while plugging my laptop into military comms port on logger I received a pretty strong shock myself(I Know!Lol). I connected a 110 volt panel light to one leg of 4-20ma output from UV unit and a neutral from dist board to other side of panel light and it lit taking full rated load(very small) but this indicates(to me???) that this voltage is capable of generating a load and in turn could have the potential to injure somebody.
The UV unit is supplied by a 220 Volt AC supply and the manufacturers are saying that having 125 Volts AC on this output is impossible as the card is fed by a 3.9VDC power supply.
Could any of you give me some advice on this or a reason why/where the 125VAC is coming from or if it has the potential to be lethal. Measuring across the 4-20 ma output on UV unit gives 14V Dc but either leg of it to earth or neutral gives 125 V AC.
Thanks in advance.
I am new to this forum and if possible I would like to get some advice on the following please.
I attended a fault on a UV unit that has a 4-20 ma output to a logger which in turn is connected to other devices giving analogue and digital signals all of which have a common negative on breakout box of logger.
A fitter changing a reed switch on a flow meter and reported that he received a substantial shock when he was replacing the reed switch which normally works at 3.9 v DC. I measured voltage on pair of wires to reed switch and recorded 3.9V DC but I did notice that my volt tick was showing high AC Voltage present, I then measured from each leg of wire to reed switch and recorded 125 Volts AC to main earth and neutral bar on distribution board.
I eventually traced the 125 V AC to 4-20 ma output on UV unit and found it had back fed via logger breakout box(common negatives) and in turn was present at all devices connected to logger. I thought at first this might be a floating/induced voltage but while plugging my laptop into military comms port on logger I received a pretty strong shock myself(I Know!Lol). I connected a 110 volt panel light to one leg of 4-20ma output from UV unit and a neutral from dist board to other side of panel light and it lit taking full rated load(very small) but this indicates(to me???) that this voltage is capable of generating a load and in turn could have the potential to injure somebody.
The UV unit is supplied by a 220 Volt AC supply and the manufacturers are saying that having 125 Volts AC on this output is impossible as the card is fed by a 3.9VDC power supply.
Could any of you give me some advice on this or a reason why/where the 125VAC is coming from or if it has the potential to be lethal. Measuring across the 4-20 ma output on UV unit gives 14V Dc but either leg of it to earth or neutral gives 125 V AC.
Thanks in advance.