Re: Higher Voltage to Ground
Pete, is this system provided by the Utility or is it derived on site? I think the issue is with the transformer supplying the system. If this is a 240/120 delta system using a single midtapped transformer the single-phase load is limited, typically to 5% of the three-phase KVA. If the contractor is using the high-leg and midtap, he could overload the neutral at the transformer winding. I do not know of any transformer designed to operate using the high-leg in conjunction with the midtap. My answer would be, if its your transformer, its not UL-Listed for this application, if it is a utility bank, you may want to ask them about such an application, I am sure they don't want their transformers loaded this way.