I am working on a brief history of significant changes to grounding
Here is what I have so far
1923 NEC - First mention of driven rod or pipe electrodes
1925 NEC - Driven rod electrodes now called ?artificial?, 8 ft long, 1/2? rod or ?? pipe
If resistance >25 ohms, requires 2 electrodes spaced 6 feet apart
1951 NEC - Ten feet of less of metal water pipe must be supplemented with additional electrode
1947 - Grounding receptacles required for laundry
1956 - Grounding receptacles required for garages, basements, outdoors
1962 - All branch circuits must include a grounding conductor
16 AWG for 12 and 14 gage circuits, 14 AWG for 10 gage circuits
1963 - Research paper presented by H.G. Ufer at IEEE Conference
1969 - Full size ground required for circuits
1971 - Water pipe electrode must be supplemented with additional electrode
1971 - Ufer ground must be used ?If Available?
1974 - NFPA TIA ?if available? does not mean it has to be used.
1999 - Additional electrode must have resistance of 25 ohms or less, or be supplemented with additional electrode
1993 - Interior metal water piping more than 5 ft from point of entrance can not be used as part of the grounding electrode system
1999? - No longer allowed to use use neutral for frames of ranges, etc
2002 - Can't reground neutral if creates a parallel path to separate buildings
2005 - Ufer ground must be used when present
2005 - Bonding added to title
2008 ? Supplementary ground rod changed to auxiliary ground rod
2008 - Ground is now the earth
2008 - Can not reground the neutral at separate buildings
Need to know: when structural steel/metal was added
When was bonding added, my 1956 NEC doesn't mention
And the above may not be 100% accurate. I don't have code books before 1968
Here is what I have so far
1923 NEC - First mention of driven rod or pipe electrodes
1925 NEC - Driven rod electrodes now called ?artificial?, 8 ft long, 1/2? rod or ?? pipe
If resistance >25 ohms, requires 2 electrodes spaced 6 feet apart
1951 NEC - Ten feet of less of metal water pipe must be supplemented with additional electrode
1947 - Grounding receptacles required for laundry
1956 - Grounding receptacles required for garages, basements, outdoors
1962 - All branch circuits must include a grounding conductor
16 AWG for 12 and 14 gage circuits, 14 AWG for 10 gage circuits
1963 - Research paper presented by H.G. Ufer at IEEE Conference
1969 - Full size ground required for circuits
1971 - Water pipe electrode must be supplemented with additional electrode
1971 - Ufer ground must be used ?If Available?
1974 - NFPA TIA ?if available? does not mean it has to be used.
1999 - Additional electrode must have resistance of 25 ohms or less, or be supplemented with additional electrode
1993 - Interior metal water piping more than 5 ft from point of entrance can not be used as part of the grounding electrode system
1999? - No longer allowed to use use neutral for frames of ranges, etc
2002 - Can't reground neutral if creates a parallel path to separate buildings
2005 - Ufer ground must be used when present
2005 - Bonding added to title
2008 ? Supplementary ground rod changed to auxiliary ground rod
2008 - Ground is now the earth
2008 - Can not reground the neutral at separate buildings
Need to know: when structural steel/metal was added
When was bonding added, my 1956 NEC doesn't mention
And the above may not be 100% accurate. I don't have code books before 1968