J jph320 Member Location Cinnaminson nj Occupation Electrician Jan 18, 2011 #1 How many 14/2 or 12/2 NM can I fit in a 1/2 in hitlock connector?
ceb58 Senior Member Location Raeford, NC Jan 18, 2011 #2 jph320 said: How many 14/2 or 12/2 NM can I fit in a 1/2 in hitlock connector? Click to expand... What is a Hitlock connector?
jph320 said: How many 14/2 or 12/2 NM can I fit in a 1/2 in hitlock connector? Click to expand... What is a Hitlock connector?
iwire Moderator Staff member Location Massachusetts Jan 18, 2011 #3 For use with double wire, nonmetallic wire. Two No. 14-2 or 2 No. 12-2, one 14-2 and one 12-2, one 14-2 and one 10-2, or one 12-2 and one 10-2. http://www.doitbest.com/Electrical+conduit-Thomas+and+Betts-model-NC501DBL5-doitbest-sku-555347.dib
For use with double wire, nonmetallic wire. Two No. 14-2 or 2 No. 12-2, one 14-2 and one 12-2, one 14-2 and one 10-2, or one 12-2 and one 10-2. http://www.doitbest.com/Electrical+conduit-Thomas+and+Betts-model-NC501DBL5-doitbest-sku-555347.dib
Nium Senior Member Location Bethlehem, PA Jan 18, 2011 #4 Nc-501sc Nc-501sc NC501SC:For use with single wire, nonmetallic wire 14 2 or 14 3, 12 2, or 12 3, or 10 2 http://www.amazon.com/Thomas-Betts-NC501SC1-Lock-Connector/dp/B000FRS9TM NC501DBLSC: As iwire said
Nc-501sc Nc-501sc NC501SC:For use with single wire, nonmetallic wire 14 2 or 14 3, 12 2, or 12 3, or 10 2 http://www.amazon.com/Thomas-Betts-NC501SC1-Lock-Connector/dp/B000FRS9TM NC501DBLSC: As iwire said