i gotta customer who does testing of food processing equipment,
and needs to test 480 volt motors from 50 to 100 HP.
he has been slamming them across the line with a non fused disconnect,
backed up by a breaker.... you know, one of those plastic hubbell
disconnects made for wet locations...
anyway, it blew off the wall, tripping the breaker, finally. some days
are like that, y'know? now, he's a little more gun shy about slamming
in a 100 hp motor with a disconnect.
a couple solutions are:
soft start
or
a fused disconnect, a variety of fuse sizes, with appropriate reducers,
downstream from a 100 hp contactor, with a limit switch on the
disconnect door to disable the contactor when the door is opened
for fuse changing.
or
a VFD, with some programmed setpoints for different motors... just
pick the motor you are going to use with a rotary switch, and hook
it up.
a 100 hp. VFD from allen bradley is about $11,000, so that's not gonna
fly well...
anybody here got ideas for something like this?
thanks...
randy
and needs to test 480 volt motors from 50 to 100 HP.
he has been slamming them across the line with a non fused disconnect,
backed up by a breaker.... you know, one of those plastic hubbell
disconnects made for wet locations...
anyway, it blew off the wall, tripping the breaker, finally. some days
are like that, y'know? now, he's a little more gun shy about slamming
in a 100 hp motor with a disconnect.
a couple solutions are:
soft start
or
a fused disconnect, a variety of fuse sizes, with appropriate reducers,
downstream from a 100 hp contactor, with a limit switch on the
disconnect door to disable the contactor when the door is opened
for fuse changing.
or
a VFD, with some programmed setpoints for different motors... just
pick the motor you are going to use with a rotary switch, and hook
it up.
a 100 hp. VFD from allen bradley is about $11,000, so that's not gonna
fly well...
anybody here got ideas for something like this?
thanks...
randy