HMCP and Bi-Metallic Overload for XFMR protection

Status
Not open for further replies.

MrJLH

Senior Member
Location
CO
While performing some NETA testing on a breaker inside one of our substations I came across a HMCP and bi-metallic overload being used to protect a three phase 75kVA transformer. Although not ideal is there any reason this installation would not be acceptable per NFPA70?

Thoughts?
 
I believe the Eaton Cutler Hammer model HMCP is itself a Thermal Magnetic Circuit Breaker, so it is a UL Listed product for the application. A bi-metallic overload, typically listed on its own (used for motor protection) is typically not listed as an assembly with an HMCP breaker unless it is in a motor starter.
From a functionality standpoint, it may be fine, but it doesn't seem that it would be a listed installation and may not comply with 110.3(C)
 
I believe the Eaton Cutler Hammer model HMCP is itself a Thermal Magnetic Circuit Breaker, so it is a UL Listed product for the application. A bi-metallic overload, typically listed on its own (used for motor protection) is typically not listed as an assembly with an HMCP breaker unless it is in a motor starter.
From a functionality standpoint, it may be fine, but it doesn't seem that it would be a listed installation and may not comply with 110.3(C)
Pretty sure that is a motor circuit protector with magnetic (instantaneous) trip only.
Product Description
Designated as Eaton’s Types GMCP and HMCP, the instantaneous-only motor circuit protector (MCP) is available in ratings from 3 A to 1200 A for motor starter sizes 0 through 8.
If that is the case, the product was listed as a motor starter and not suitable for protecting a transformer.
 
AFAIK, the HMCP (and the MCP) are instantaneous-only breaker with no thermal element. They can only be used in a combination motor starter in conjunction with a motor overload relay. In my opinion, using this for transformer protection, even with the addition of the overload relay would be a violation of the UL listing for the HMCP.
 
No, it’s not going to meet Code.

HMCPs are NOT UL listed, they are UL Recognized components that can only be used as part of a factory assembled and listed motor starter assembly. There is no other approved use. So anything else will be a violation of 110.3(B).

Besides, an OL relay only acts to drop out the coil circuit if a contactor in the motor starter. Without the contactor, it does nothing.
 